est 3 network
Posted: Mon Sep 17, 2012 3:24 pm
by calebking
hi
can anyone help with a 32 est3 panel network. a few years ago the panles would drop off-line then lock up and had to be restarted. we scoped the panels and changed a few repeaters and netwoek cards. we also found the earth wasnt in A-class. so we re-cabled the whole network in 2.5mm shielded copper cable and bounded the earth at 1 panel and left floating around the rest. this worked and system stayed clear for a year but lately has returned. the panles all drop of line the restore straight away but network is unstable. any help would be great
cheers
john
Re: est 3 network
Posted: Tue Dec 18, 2012 5:32 am
by briac
good day,
please check first the lengh of the cable then the routing mode, check also if there is a power cable or gamma ,X ray influence around your system network,
the made ​​to weaken it may be due to the installation instructions,the cable is gray if the glass is exposed to heat humidity and may be moisture
Re: est 3 network
Posted: Tue Dec 18, 2012 6:43 pm
by FireTech
I used to be a "Site Tech" for an Est3 network that was 30-40 Nodes. Question..... If you look at the History or Print out after one of these "Panel Drop Outs" , does it start with the same Node number?
Also.... Here is what you Look at:
1-) Is 485 cards "seated" properly behind CPU? Is the White nylon screw installed in EVERY 485 card?
2-) Do you have any panels that have a long distance between them? If yes, How Far Apprx?