When these SD Duct smks go into Mait Alert, I "Douche" the Siga-SD. Meaning, open up the detector and give a couple bursts of air around / inside detector. But that is almost useless. I have found that the customer has to First Replace the filters in the Duct work where the detector is dirty. (Filters dirty). If Duct work is all filthy with drywall dust , etc from recent construction, Well... They gotta get them cleaned...(The duct work)
I will try and find sd cutsheet on cleaning. i have it somewhere, but i cant find it right now.....
SIGA-SD Maintenance Alert
Re: SIGA-SD Maintenance Alert
See Attach Document(s) Re--Siga-SD Cleaning / Testing Methods...
- Attachments
-
- SigaSD Cleaning pg1.pdf
- (431.23 KiB) Downloaded 1333 times
-
- Siga-SD Cleaning and Testing PG2.pdf
- How to Clean Duct Smoke
- (211.98 KiB) Downloaded 1207 times
Re: SIGA-SD Maintenance Alert
In Reviewing the Siga-SD Cleaning Attachment Instructions, It says to take the Slc Loop off (Pwr Down) Take the entire board out and clean everything thoroughly. I only clean like this if needed. (IE- You can visibly see dirt/contaminants in the detector.) Like I said Previously,
"When these SD Duct smks go into Mait Alert, I "Douche" the Siga-SD. Meaning, open up the detector and give a couple bursts of air around / inside detector. But that is almost useless. I have found that the customer has to First Replace the filters in the Duct work where the detector is dirty. (Filters dirty). If Duct work is all filthy with drywall dust , etc from recent construction, Well... They gotta get them cleaned...(The duct work)"
"When these SD Duct smks go into Mait Alert, I "Douche" the Siga-SD. Meaning, open up the detector and give a couple bursts of air around / inside detector. But that is almost useless. I have found that the customer has to First Replace the filters in the Duct work where the detector is dirty. (Filters dirty). If Duct work is all filthy with drywall dust , etc from recent construction, Well... They gotta get them cleaned...(The duct work)"
Re: SIGA-SD Maintenance Alert
Thanks JimM.
After thoroughly cleaning the detector, the next day a map fault occurred. Diagnostics shows that the device personality had changed. Is this normal that you would need to reinitialize the loop and rectify after cleaning?
After thoroughly cleaning the detector, the next day a map fault occurred. Diagnostics shows that the device personality had changed. Is this normal that you would need to reinitialize the loop and rectify after cleaning?
Re: SIGA-SD Maintenance Alert
I know you said the Personality Code Changed, But I still want to mention the SD Cover. If that Clear Cover isn't secured properly, It gives you awkward Troubles. I did see in some documentation where you have to restart the SDC card after the cleaning process. I thought this was to get rid of Environmental compensation signal though. I am curious though..... What was the personality code? And what was the Personality Code changed too? Was it the Sensitivity that Changed? IE-- From Least Sensitive to Normal Sensitive?
Make sure Clear Cover is on Good, Restart SDC card device is on. If not, let me know......
Make sure Clear Cover is on Good, Restart SDC card device is on. If not, let me know......
Re: SIGA-SD Maintenance Alert
Wait a Minute... you said Map fault.... Did you remove the SLC Wires When Cleaning? If So, Did you put the wires back exactly the way they were? Wiring changes, Map changes Hence..... Map fault.......
Re: SIGA-SD Maintenance Alert
Sorry for the delay in replying. The answer is that I did not remove the SLC loop wiring when cleaning. The device status display at the FACP showed the detector had returned from 80% dirty to 0% dirty. The map uploaded in the SDU showed the device red and indicated in its properties that the personality changed from a 1 (N/O Latching class b) to a personality of 3 (N/O Non-latching class b). I committed the expected, converted and downloaded. The detector has been normal since then.