what type of smoke is the sim-intl connected to?
a 6250B smoke?

I am thinking it is the alarm current that the smokes draw in alarm is not enough to trip the sim-init
riztgh
Posts: 11
Joined: Sat Oct 15, 2016 2:58 am

Re: SIM-INTL

Post by riztgh »

Hi,
We use 9102C type smoke detector. Datasheet attached.. Please help me. Thanks for replying.
Attachments
C-9102_Conventional_Optical_Detector.pdf
(206.41 KiB) Downloaded 671 times
riztgh
Posts: 11
Joined: Sat Oct 15, 2016 2:58 am

SIM-INTL

Post by riztgh »

HI ALL,
SIGA-CT1 +SIM-INTL INSTALLED, BUT WHEN WE CREATE ALARM IN ONE DETECTOR, IT DOES NOT TRIGGER SIGA-CT1. AS SOON AS, WE CREATE ALARM IN TWO OR MORE DETECTORS , IT TRIGGERS SIGA-CT1. HOW TO RECTIFY THIS?
Attachments
SIM-INTL.PDF
(78.55 KiB) Downloaded 1525 times