Drill Button- Notifier 3030

Post Reply
maverick
Posts: 10
Joined: Mon Nov 11, 2013 1:40 pm

Drill Button- Notifier 3030

Post by maverick »

In one of the site , after pressing the drill button from Panel ,Some of the floors hooter are getting activate but not for all the floors. As per the requirement all Floors hooter should activate in case of Drill.

Could you please provide the reason & possible cause for this problem?

Also share what we need to check in software database and at panel & Field end to rectify the issue.

Looking forward the reply on ASAP basis.

Thanks
pyrosucks
Posts: 106
Joined: Wed Feb 23, 2011 9:08 am

Re: Drill Button- Notifier 3030

Post by pyrosucks »

DRill button does not activate addressable control modules, only on board nacs
Leo
Site Admin
Posts: 887
Joined: Thu Dec 11, 2008 7:52 am

Re: Drill Button- Notifier 3030

Post by Leo »

I think the nfs-3030 does not have on board nac but the nfs2-3030 (newer version) has one
are all or some of the control modules not turning on?
are the control modules programmed the same
if you trip a alarm and hit alarm silence what happens. do all the H/S stop, do the horns stop and the strobe stay on, does half the building still ring?
Post Reply