Search found 33 matches

by peermoh80
Wed May 08, 2013 11:25 pm
Forum: NICET, NPFA72/70, State License
Topic: NFPA72 - Smoke Detector vs Smoke Alarm
Replies: 4
Views: 7302

Re: NFPA72 - Smoke Detector vs Smoke Alarm

Mr.Leo,

clause 29.8.4.4 NFPA 2010 "In rooms with open joists or beams, all ceiling-mounted detectors or alarms shall be
located on the bottom of such joists or beams."


is above clause applicable for spot type smoke detector?
by peermoh80
Tue May 07, 2013 9:14 am
Forum: NICET, NPFA72/70, State License
Topic: Smoke detector drop down from ceiling
Replies: 5
Views: 7749

Re: Smoke detector drop down from ceiling

Hi Mr.Leo,

iam realy looking for your answer for the above which i trust only you can expline about the stated issue.
by peermoh80
Tue May 07, 2013 9:09 am
Forum: NICET, NPFA72/70, State License
Topic: Smoke detector drop down from ceiling
Replies: 5
Views: 7749

Re: Smoke detector drop down from ceiling

[quote="peermoh80"]Hi Mr.Leo, I found the clause 29.8.4.4 NFPA 2010 "In rooms with open joists or beams, all ceiling-mounted detectors or alarms shall be located on the bottom of such joists or beams." As per this i think the installation is correct. whats you suggestion.[/quot H...
by peermoh80
Mon Apr 22, 2013 1:56 am
Forum: EST3
Topic: recommended distance from valves supervisory switch and modu
Replies: 1
Views: 2218

recommended distance from valves supervisory switch and modu

Hi All,

What is the recommended distance from FF valves supervisory switch and modules(Siga-CT1/CT-2).
by peermoh80
Mon Apr 01, 2013 3:21 am
Forum: NICET, NPFA72/70, State License
Topic: Smoke detector drop down from ceiling
Replies: 5
Views: 7749

Re: Smoke detector drop down from ceiling

Hi Mr.Leo,

I found the clause 29.8.4.4 NFPA 2010 "In rooms with open joists or beams, all ceiling-mounted detectors or alarms shall be
located on the bottom of such joists or beams."

As per this i think the installation is correct.

whats you suggestion.
by peermoh80
Mon Apr 01, 2013 1:46 am
Forum: NICET, NPFA72/70, State License
Topic: Smoke detector drop down from ceiling
Replies: 5
Views: 7749

Re: Smoke detector drop down from ceiling

Thanks for your reply. at site its a cinema hall having ceiling height of 18.5 mtr from ffl. at site we fix smoke detector from the celing 3.7 mtr. our third party saying the same clauses you mentioned and reject the installation. Pls guide is acceptable by NFPA 72 and how i can convince the third p...
by peermoh80
Tue Feb 19, 2013 12:56 am
Forum: NICET, NPFA72/70, State License
Topic: Smoke detector drop down from ceiling
Replies: 5
Views: 7749

Smoke detector drop down from ceiling

Hi guys,

can any one guide me what is the max distance, smoke detector can drop down from the ceiling as per NFPA-72.

as i chek in NFPA its shown only max 300mm height from ceiling if its fix on wall.

pls guide.
by peermoh80
Sun Jun 24, 2012 5:41 am
Forum: EST3
Topic: can any one help me to find wiring drawing
Replies: 0
Views: 2241

can any one help me to find wiring drawing

i need a wiring drawing showing that Siga-CR and Siga-CT2 connecting to HVAC FAN's and Damper.

Thanks
by peermoh80
Wed Jun 20, 2012 11:10 pm
Forum: EST3
Topic: Country of origin for EST3 Feild Devices
Replies: 0
Views: 2095

Country of origin for EST3 Feild Devices

Any one have Country of origin for Complete EST3 Feild Devices
by peermoh80
Mon Jun 11, 2012 6:24 am
Forum: EST3
Topic: what is the maximum o/p ckt from APS6A
Replies: 1
Views: 2342

what is the maximum o/p ckt from APS6A

what is the maximum o/p ckt from APS6A